First you need to remove all the old refrigerant by pulling the system down to a vacuum as close to 30 in/hg as possible at your elevation to remove all the refrigerant, air, and water from the system. this needs to be held for at least 20min.
With the system under vacuum you need to hold it for at lease 5 min to check for any leaks, drop in vacuum means a leak.
Then while the system is under vacuum you need to inject oil, just a couple ounces more than you removed with the evacuation of the system, followed by a critical charge (means you need to weigh the refrigerant).
this is a VERY simplified version of a proper A/C system recharge, it doesn't include refrigerant recovery which if you don't recover can get you in trouble if the EPA sees you releasing it.
I would suggest taking it to a shop, unless of course you have the proper equipment to properly weight the refrigerant to ensure a proper charge, something that can't be accurately measured with gauge pressures, and an accurate set of gauges to watch the vacuum readings.